bdmowers Posted November 6, 2019 Report Share Posted November 6, 2019 I would appreciate some electrical advice. I want to use a 2-station electrical burner. It uses 1600 watts and is 60Hz. and 127v. I have 2 electrical boxes. They both say 60Hz and "50 a maximo". They re both 1 fase and one is 2 hilos and the other 3 hilos. Would I be able to plug in this 2-burner in an outlet that is connected to one of these boxes without blowing it out? I donpt know if I gave all of the requisite information about the boxes. Thank you! Quote Link to comment Share on other sites More sharing options...
Go Solar Posted November 6, 2019 Report Share Posted November 6, 2019 The electric hotplate math works out to 12.6 amps (1600 / 127). The question is not if you have enough main panel supply, as with 2 x 50 amp you should be fine,.....however good to check the wiring gauge to where you will plug in the hotplate. If you've used a toaster, electric kettle, toaster oven or similar in the same location, it should be OK, as a kitchen circuit "should" be setup for and rated for at least 15 amps..... Quote Link to comment Share on other sites More sharing options...
bdmowers Posted November 6, 2019 Author Report Share Posted November 6, 2019 24 minutes ago, Go Solar said: The electric hotplate math works out to 12.6 amps (1600 / 127). The question is not if you have enough main panel supply, as with 2 x 50 amp you should be fine,.....however good to check the wiring gauge to where you will plug in the hotplate. If you've used a toaster, electric kettle, toaster oven or similar in the same location, it should be OK, as a kitchen circuit "should" be setup for and rated for at least 15 amps..... Thanks, Go. I should add that the 2 boxes are widely separated in space and are not connected in any way. One box serves one side of the house and the other serves the other. I would be plugging in the hotplates to a thick extension cord that will be plugged in to an outlet that is right next to one of the boxes. Will that work? Can I plug another of the 2 burners in to an outlet that is connected to the other box, at the same time or is that a bit risky? Quote Link to comment Share on other sites More sharing options...
Go Solar Posted November 6, 2019 Report Share Posted November 6, 2019 Based on your description, should be fine - however, if you're not electrically inclined, why not have someone who is, check it? Fast and easy to do, can't do it via this board.... Suerte. Quote Link to comment Share on other sites More sharing options...
bdmowers Posted November 6, 2019 Author Report Share Posted November 6, 2019 1 hour ago, Go Solar said: Based on your description, should be fine - however, if you're not electrically inclined, why not have someone who is, check it? Fast and easy to do, can't do it via this board.... Suerte. Thanks so much, GoSolar. Quote Link to comment Share on other sites More sharing options...